I’m facing a classic problem that I just can’t seem to solve: the UPS doesn’t shut down (doesn’t cut power to the outlets) after the TrueNAS SCALE server is completely powered off, which causes the battery to drain completely.
System configuration:
• OS: TrueNAS SCALE 25.10.7
• UPS: Powercom RPT-2000 (Raptor)
• Connection: USB cable
The server detects the UPS without any issues and correctly reads the charge percentage, voltage, and load. When the power goes out, TrueNAS initiates the shutdown procedure via a timer and shuts down the TrueNAS SCALE correctly. However, during the final stage, the UPS does not receive (or ignores) the shutdown command. The UPS display and LEDs remain lit, power remains at the outlets, and the UPS continues to operate until the batteries are completely drained.
In the UPS service settings, the “Power Off UPS” option is enabled, and the operating mode is set to “Master.”
Which driver is currently considered the most stable for the RPT series on recent versions of SCALE—blazer_usb or nutdrv_qx?
What additional parameters (Auxiliary Parameters) do I need to specify in ups.conf to ensure the shutdown command goes through? (Perhaps something like subdriver=cypress, offdelay, or runtime?)
I’d really appreciate any help from Powercom owners who’ve managed to get this connection working properly!
AFAIK, the UPS does not “shutoff”. Generally you want to set you system to power off when ups battery is low, with most ups’s that is 10%-20%, after the server is powered off, there should be no drain on the UPS. I have been in IT for 40 years and have never heard of a ups powering itself off, or a ups “completely draining” with just the LEDs on.
From the users manual:
On its own, the Raptor keeps the outlets powered through an outage and only cuts them when the battery is fully used up.
Power outage: The outlets stay on. If mains voltage drops out or goes outside the AVR range, the connected equipment runs from the UPS battery. On the RPT-2000AP all 6 outlets are battery-backed, so none are surge-only.
Low battery: The UPS beeps and keeps powering the outlets until the battery is empty. Below 30% charge it beeps fast, twice a second, until it shuts down from full discharge or mains power returns. The manual gives no separate low-battery cutoff for the outlets. There are three other ways the output gets cut:
1-hour limit: To protect the battery, the UPS shuts down after 1 hour on battery. This could matter with a light load
Green Mode: With no load in battery mode, the UPS turns itself off, and it turns back on when mains power returns. Watch for this with very small loads. In one review, a UPS with a 25 W load shut off after about 7 minutes, apparently because the monitoring software had turned Green Mode on.
There are a couple more devices connected to the UPS, but I’m wondering how to turn off the UPS after the Truenas Scale has shut down. This is because when power is restored—and the UPS continues to run after the Truenas Scale has shut down—the server doesn’t turn on automatically since the UPS wasn’t turned off.
If i check the option in my nut service settings my ups powers off after everything shut down. My truenas is nut master and my opnsense is set as slave, works perfectly fine…